06-28-2020, 01:19 AM
Here are programs made for a basic Control Systems class.
Summary
1. Controllability (ctrb) and Is controllable? (isctrb)
2. Observability (obsv) and Is observable? (isobsv)
3. Ackermann's Formula (ACKER)
4. Statespace to Transfer Function (ss2tf)
5. Transfer Function to Statespace (tf2ss)
6. Routh-Hurwitz Criterion (rhs)
7. Static Error Constants, Steady State Error, and System Type (sterr)
8. Second Order System Fundamentals (solveFund)
9. Step Function (stp)
10. Step Info (stepInfo)
1. The first program will take as input the system matrix (a) and the input matrix (b) to find the controllability matrix. With it there is another function that will check if the controllability matrix found is controllable or not.
2. The next program will take the system matrix (a) and the output matrix (c) as inputs to find the observability matrix. Along with it is another function to check if the observability matrix is observable.
3. This function below uses Ackermann's Formula to find the feedback constants. This function requires the use of the CTRB(a,b) function. It takes as input the system matrix (a), the input matrix (b), and the desired characteristic equation coefficients.
Changed determinate to determinant
4. This program converts the system from a statespace model to a transfer function. It takes as arguments the system matrix (a), the input matrix (b), the output matrix (d) and the feedthrough matrix (d).
5. This program converts the system from a transfer function to statespace form. It takes as inputs the numerator and denominator either as a function or as a vector containing the coefficients. The third input (form) is either 0 for Phase-Variable form and 1 for observable canonical form. It only outputs the system matrix (a). To output the other matrices just insert b, c, and d into the CAS console. If you want to check the statespace with MATLAB's take the transpose of the output of form 1.
6. This program creates the Routh table from the characteristic equation. Insert the characteristic equation as a function of s or as a list or vector of coefficients. You can also enter the system matrix (a) instead of the characteristic equation. This program uses the CAS so if you want to find k just enter k, but you may have to simplify the answer within the table.
Tries to take care of the Epsilon Method (where zero is in first column) and Polynomial Method (Row of Zeros). Does not take into account the reverse coefficient method - this would have to be entered by the user.
There also may be differences as someone may simplify in different ways compared to what is in this table. Also take into consideration if working with numbers if you don't get the correct results in exact mode you may be able to receive the correct results in approximate mode due to simplification.
Updated to account for a characteristic equation with the second element being zero resulting in undefined.
Fixed a two by two routh matrix whose determinant is equal to zero from using row of zeros function instead of epsilon
7. The program sterr takes the transfer function (xfcn) and input signal (inp) as inputs. Normally the input signal constant will be 1 but you can change this to any number. This program will find the Static Error Constants (Kp - position, Kv - velocity, Ka - acceleration) and also finds their respective steady state errors (essp - step, essv - ramp, essa - parabola). The program also tells you the system type (0 - (s^0 = 1) step, 1 - (s^1 = s) ramp, 2 - (s^2) parabola). Outputs a table containing all the above information.
8. This program tries to solve for all possible input combinations to solve for a second order system. Inputs are s, zeta, wn, perOS, Tr, Tp, and Ts with the leftmost variable taking precedence. It will output s, zeta, wn, perOS, Tr, Tp, Ts, K, and the transfer function.
Please be aware that the equations to solve the system may not exactly adhere to what you may be using. For example, Settling time (Ts) is solved within 2% of the final value. The equation to solve for that can either be -ln(0.02)/zeta*wn or approximately 4/zeta*wn.
Added negative in front of sigma variable in case where Tp and Ts are given
9. The stp (step) program graphs the step response of the transfer function. It takes as input the transfer function, gain, and a boolean for if the system is an open loop or closed loop unity feedback system.
*This program is a bit unstable and may cause your calculator to crash* Reasons for this may be due to the complexities of the transfer function or errors within or when running the program.
HP Prime G1 users may have troubles with underdamped systems. Unfortunately, I cannot find a way to always distinguish between infinity and undefined.
*HP Prime G2 users may not always experience the same issue.*
The program outputs the step response plot in F2, the upper and lower rise time F4 and F5, the upper and lower settling times (within 2% of final value) F7 and F8, and the final value F0. These are provided in case stepInfo is innacurate, verify, or prefer to find the values manually.
10. The step info (stepInfo) program tries to find the step response characteristics of the step response graph. It has no input, and outputs a table containing the Rise Time (Tr), Peak Time (Tp), Peak Value, Settling Time, Settling Value, Percent Overshoot, and Final Value.
This program may take a while to run, and may be unstable. From my experience it seems to run faster when "Use i to factor polynomials" or the "Use i:" CAS setting is unchecked.
This program requires the Step function (stp) to be run first.
If it returns error or incorrect results you can try repositioning the step response plot and running it again.
Summary
EXPORT CTRB(a,b)
LOCAL k,Cm,Cmsolve;
IF (rowDim(a) == colDim(a) AND rowDim(a) == rowDim(b) AND SIZE(SIZE(b)) >1) THEN
Cm := MAKEMAT(0,rowDim(a),rowDim(a)*colDim(b));
FOR k FROM 1 TO rowDim(a) DO
Cmsolve := a^(k-1)*b;
Cm := REPLACE(Cm,{1,k*colDim(b)-(colDim(b)-1)},Cmsolve);
ELSE
RETURN "Matrix A should be square, and the rows of Matrices A and B should have the same amount of elements.";
RETURN Cm;
EXPORT isctrb(Cm)
IF (abs(DET(Cm)) >= 1 AND RANK(Cm) == rowDim(Cm)) THEN
RETURN "Controllable";
ELSE
RETURN "Uncontrollable";
EXPORT OBSV(a,c)
LOCAL k,Om,Omsolve;
IF (SIZE(SIZE(c)) == 1) THEN
c := TRN(list2mat(c,1));
Om := MAKEMAT(0,rowDim(a)*rowDim(c),rowDim(a));
IF (rowDim(a) == colDim(a) AND rowDim(a) == colDim(c)) THEN
Omsolve := c*a^(k-1);
Om := REPLACE(Om,{k*rowDim(c)-(rowDim(c)-1),1},Omsolve);
ELSE
RETURN "Matrix A should be square, and the columns of Matrices A and C should have the same amount of elements.";
RETURN Om;
EXPORT isobsv(Om)
IF (abs(DET(Om)) >= 1 AND RANK(Om) == rowDim(Om)) THEN
RETURN "Observable";
ELSE
RETURN "Unobservable";
EXPORT ACKER(a,b,ce)
LOCAL c,cm,sc,sP,cemsolve,p,icm,k;
cm := CTRB(a,b);
IF (abs(DET(cm)) >= 1 AND RANK(cm) == rowDim(a)) THEN
sP := SIZE(ce);
sP := sP(1);
cemsolve := 0;
p := revlist(ce);
sc := SIZE(cm);
sc := sc(1);
c := [0];
FOR W FROM 1 TO sc-2 DO
c := append(c,0);
c := append(c,1);
FOR Q FROM sP DOWNTO 1 DO
cemsolve := cemsolve+p(Q)*a^(Q-1);
icm := inv(cm);
k := c*icm*cemsolve;
RETURN k;
ELSE
RETURN "System is uncontrollable, the determinant is zero and the rank does not match the system matrix";
#cas
ss2tf(a,b,c,d) :=
LOCAL tfnum,tfden,tfmonic,tftemp,tf,k,q;
IF TYPE(SIZE(c)) == 0 THEN
CASE
IF (TYPE(d) == 0 OR TYPE(d) == 3) THEN d := [[d]] END;
IF (TYPE(SIZE(d)) == 0) THEN d := TRN(d) END;
DEFAULT BREAK END;
IF (rowDim(a) == colDim(a) AND rowDim(b) == colDim(c) AND rowDim(a) == rowDim(b) AND rowDim(a) == colDim(c) AND (SIZE(d) == [1, 1] OR (colDim(d) == colDim(b) AND rowDim(c) == rowDim(d)))) THEN
tf := (c*(((s*IDENMAT(rowDim(a)))-a)^-1)*b)+d;
FOR k FROM 1 TO rowDim(d) DO
FOR q FROM 1 TO colDim(d) DO
tftemp := tf(k,q);
tfnum := numer(tftemp);
tfden := denom(tftemp);
tfmonic := coeff(tfden,s)(1);
tfnum := approx((tfnum)/tfmonic);
tfden := approx((tfden)/tfmonic);
tfnum := expand(tfnum);
tfden := expand(tfden);
tftemp := [tfnum/tfden];
tf := REPLACE(tf,{k,q},tftemp);
tf := approx(exact(tf));
ELSE
RETURN "The number of rows and columns in Matrix A need to match those in B and C respectively. The rows and columns of the D Matrix need to match C and B respectively."
IF (SIZE(d) == [1, 1]) THEN
tf := tf(1,1);
ELSE
RETURN tf;
#end
#cas
tf2ss(num,den,form) :=
LOCAL A1,A2,Ai2,sA1,Snum,Aden;
CASE
IF (TYPE(SIZE(num)) == 4 OR TYPE(SIZE(den)) == 4) THEN RETURN "Numerator and Denominator must be vectors"; END;
IF TYPE(den) == 8 OR TYPE(num) == 8 THEN
Aden := expand(den);
Aden := symb2poly(den,s);
Snum := expand(num);
Snum := symb2poly(num,s);
Snum := EXPR(STRING(Snum));
Aden := EXPR(STRING(Aden));
IF TYPE(den) == 0 OR 1 OR 4 OR 6 OR TYPE(num) == 0 OR 1 OR 4 OR 6 THEN
Aden := den;
Snum := num;
DEFAULT RETURN "Args should be poly/(s-p1)*(s-pn) or list/vector";
IF (Snum == Aden) THEN RETURN "Numerator is the same as the denominator"; END;
WHILE SIZE(Snum) < SIZE(Aden) DO
Snum := INSERT(Snum,1,0);
IF SIZE(Snum) == SIZE(Aden) THEN BREAK; END;
Snum := approx(Snum./Aden(1));
Aden := approx(Aden./Aden(1));
CASE
IF (form == 0) THEN
A1 := -(REVERSE(Aden));
sA1 := size(A1)-1;
A2 := A1(1..(sA1));
Ai2 := IDENMAT(sA1);
a := ADDROW(Ai2,A2,sA1+1);
a := DELROW(a,1);
b := MAKEMAT(0,sA1,1);
b := REPLACE(b,sA1,[1]);
qrinfo := quorem(Snum,Aden);
c := qrinfo(2);
d := TRN(TRN(qrinfo(1)));
IF (SIZE(qrinfo(2)) != rowDim(a)) THEN
WHILE SIZE(qrinfo(2)) < rowDim(a) DO
c := INSERT(c,1,0);
IF SIZE(c) == rowDim(a) THEN BREAK; END;
c := TRN(TRN(revlist(c)));
RETURN a;
IF (form == 1) THEN
A1 := -(Aden);
sA1 := size(A1)-1;
A2 := A1(2..(sA1+1));
a := ADDCOL(Ai2,A2,1);
a := DELCOL(a,sA1+1);
b := qrinfo(2);
IF (SIZE(qrinfo(2)) != rowDim(A3)) THEN
b := INSERT(b,1,0);
IF SIZE(b) == rowDim(a) THEN BREAK; END;
b := TRN(b);
c := MAKEMAT(0,1,sA1);
c := REPLACE(c,1,[1]);
RETURN a;
DEFAULT RETURN "Invalid form, choose 0 for Phase Var. Canonical or 1 for Obsv. Canon. Form"
#end
#cas
rhs(ce) :=
LOCAL rh,sumsrhb,srhb,ssprh,ct,Srh,nPFlag,scol;
LOCAL csprh,csprhlist,order,q,w,rhdet,sprh,sprhcheck;
LOCAL qw;
CASE
IF TYPE(ce) == 8 AND TYPE(SIZE(ce)) == 0 THEN ce := coeff(ce,s); END;
IF TYPE(ce) == 4 AND TYPE(SIZE(ce)) == 4 THEN ce:= coeff(det(s*IDENMAT(rowDim(ce))-ce),s); END;
IF TYPE(ce) == 4 OR TYPE(ce) == 6 AND TYPE(SIZE(ce)) == 0 THEN ce:=ce END;
DEFAULT RETURN "The characteristic equation needs to either be an equation, list/vector, or a system matrix (a)"; END;
nPFlag := 0;
IF ce(2) == 0 THEN
ce(2):= ɛ;
IF odd(SIZE(ce)) THEN
rh := TRN(list2mat(ce,2));
ELSE
ct := MAKEMAT(0,SIZE(ce)-rowDim(rh),colDim(rh));
FOR q FROM 1 TO rowDim(ct) DO
rh := ADDROW(rh,ct(q),(1+rowDim(rh)));
Srh := colDim(rh);
FOR q FROM 1 to rowDim(rh) DO
IF (MIN(rh(q)) != 1 AND MIN(rh(q)) != 0) THEN
srhb := (rh(q)/content(rh(q)));
sumsrhb := ΣLIST(srhb);
IF FP(sumsrhb) == 0 AND FP(srhb(q)) == 0 THEN
REPLACE(rh,{q,1},srhb);
rh := ADDCOL(rh,mat2list(MAKEMAT(0,rowDim(rh),1)),colDim(rh)+1);
FOR q FROM 1 TO SIZE(ce)-2 DO
ssprh := rh(q+1);
IF MIN(ssprh) != 1 AND FP(MIN(ssprh)) == 0 AND SIZE(remove(0,ssprh)) != 1 THEN
ssprh := ssprh/content(ssprh);
sprh := ssprh;
REPLACE(rh,{q+1,1},sprh);
ELSE
sprh := ssprh;
sprhcheck := rh(q);
sprhcheck := sprhcheck/content(sprhcheck);
FOR w FROM 1 TO Srh DO
rhdet := -det([[rh(q,1),rh(q,w+1)],[rh(q+1,1),rh(q+1,w+1)]])/rh(q+1,1);
IF nPFlag == 0 THEN
IF (SIZE(ce) != 4 AND w == 1 AND rhdet == 0 AND (sprh == sprhcheck OR ΣLIST(abs(sprh) .- abs(sprhcheck)) == 0) OR DIFFERENCE(abs(sprh) .- abs(sprhcheck)) == 0) THEN
order := rowDim(rh)-2-(q-1);
csprhlist := {};
FOR qw FROM 1 TO SIZE(sprh) DO
csprh := sprh(qw)*s^order;
csprhlist := CONCAT(csprhlist,csprh);
order := order-2;
csprhlist := diff(csprhlist,s);
csprhlist := ΣLIST(csprhlist);
csprhlist := remove(0,coeff(csprhlist,s));
IF SIZE(csprhlist) != 1 THEN
csprhlist := csprhlist/content(csprhlist);
REPLACE(rh,{q+2,1},csprhlist);
q := q+1;
w:= 1;
nPFlag := 1;
IF (w == 1 AND rhdet == 0 AND (sprh != sprhcheck OR SIZE(ce) == 4)) THEN
rhdet := ε;
REPLACE(rh,{q+2,w},[rhdet]);
scol := MAKELIST(s^q,q,rowDim(rh)-1,0);
ADDCOL(rh,scol,1);
DELCOL(rh,colDim(rh));
RETURN simplify(rh);
#end
#cas
sterr(xfcn,inp) :=
LOCAL kp,essp,kv,essv,ka,essa,ty;
LOCAL sterrlabel,sterrval;
kp := limit(xfcn,s,0);
essp := (inp*1/(1+kp));
kv := limit(s*xfcn,s,0);
essv := (inp*1/kv);
ka := limit(s^2*xfcn,s,0);
essa := (inp*1/ka);
IF ((kv == 0 AND essv == ±∞ OR ∞) AND (ka == 0 AND essa == ±∞ OR ∞)) THEN ty := 0; kp := approx(kp); essp := approx(essp); END;
IF ((kp == ±∞ OR ∞ AND essp == 0) AND (ka == 0 AND essa == ±∞ OR ∞)) THEN ty := 1; kv := approx(kv); essv := approx(essv); END;
IF ((kp == ±∞ OR ∞ AND essp == 0) AND (kv == ±∞ OR ∞ AND essv == 0)) THEN ty := 2; ka := approx(ka); essa := approx(essa); END;
sterrlabel := list2mat({"Static Error Constant","Kp","Kv","Ka","Type"},1);
sterrval := {"Static Error Constant Value",kp,kv,ka,ty};
sterrlabel := ADDCOL(sterrlabel,sterrval,2);
sterrval := {"Static Error", "essp", "essv", "essa","----------"};
sterrlabel := ADDCOL(sterrlabel,sterrval,3);
sterrval := {"----------",essp,essv,essa,"----------"};
sterrlabel := ADDCOL(sterrlabel,sterrval,4);
RETURN sterrlabel;
#end
#cas
solveFund(s,zeta,wn,perOS,Tr,Tp,Ts) :=
LOCAL sigma,wd,funlabel,funval,k,xfcn;
CASE
IF s THEN
zeta := MAX(solve(-(RE(s)/IM(s))^2*z^2+(RE(s)/IM(s))^2=z^2,z));
wn := -RE(s)/zeta;
perOS := exp((-zeta*3.1415926539)/(sqrt(1-zeta^2)))*100;
Tr := (1.76*zeta^3-0.417*zeta^2+1.039*zeta+1)/wn;
Ts := -ln(0.02)/(zeta*wn);
Tp := 3.1415926539/IM(s);
IF zeta AND Tr THEN
wn := (1.76*zeta^3-0.417*zeta^2+1.039*zeta+1)/Tr;
s := -zeta*wn+(wn*sqrt(1-zeta^2))*i;
Tp := 3.1415926539/(wn*sqrt(1-zeta^2));
IF zeta AND Tp THEN
wn := 3.1415926539/(Tp*sqrt(1-zeta^2));
IF zeta AND Ts THEN
wn := (-ln(0.02*sqrt(1-zeta^2))/(zeta*Ts));
IF zeta AND wn THEN
IF wn AND perOS THEN
zeta := -ln(perOS/100)/(sqrt(3.1415926539^2+(ln(perOS/100))^2));
IF wn AND Tr THEN
zeta := MAX(RE(solve((1.76*z^3-0.417*z^2+1.039*z+1)/Tr=wn,z)));
IF wn AND Tp THEN
zeta := MAX(fsolve((3.1415926539/(Tp*sqrt(1-z^2)))=wn,z));
IF wn AND Ts THEN
zeta := MAX(fsolve((-ln(0.02*sqrt(1-zeta^2))/(z*Ts))=wn,z));
IF Tr AND perOS THEN
IF Tr AND Tp THEN
zeta := MIN(fsolve((1.76*z^3-0.417*z^2+1.039*z+1)/Tr=3.1415926539/(Tp*sqrt(1-z^2)),z));
IF Tr AND Ts THEN
zeta := MAX(RE(fsolve((1.76*z^3-0.417*z^2+1.039*z+1)/Tr=(-ln(0.02)/(z*Ts)),z)));
IF Tp AND perOS THEN
IF Tp AND Ts THEN
sigma := -ln(0.02)/Ts;
wd := 3.1415926539/Tp;
s := -sigma+wd*i;
IF Ts AND perOS THEN
wn := -ln(0.02)/(zeta*Ts);
DEFAULT RETURN "This combination of inputs does not provide enough information!"; END;
k := wn^2;
xfcn := 0;
funlabel := list2mat({"S (σ+*ωd)", "Zeta (ζ)", "Natural Frequency (ωn)", "Percent Overshoot (%OS)", "Rise Time (Tr)", "Peak Time (Tp)", "Settling Time (Ts)"},1);
funval := {s,zeta,wn + " rad/s",perOS + " %",Tr + " s",Tp + " s",Ts + " s"};
funlabel := ADDCOL(funlabel,funval,2);
purge(s);
xfcn := k/(s^2+2*zeta*wn*s+k);
REPLACE(funlabel,{9,2},[xfcn]);
RETURN funlabel;
#end
#cas
stp(xfcn,k,typesys) :=
LOCAL Gfn,Hfn,usrg,dxfcn,nxfcn,roots,ceroots,minev;
LOCAL Tfs,y,Tfinal;
F2 := "";
F4 := "";
F5 := "";
F7 := "";
F8 := "";
F0 := "";
Gfn := xfcn;
Hfn := 1;
IF (k <= 0) THEN
RETURN "Gain (K) must be greater than or equal to one (1). If gain is already taken into account in the transfer function then leave as one (1)";
CASE
IF (typesys == 0) THEN
solveTf := (k*Gfn);
IF (typesys == 1) THEN
solveTf := ((k*Gfn)/(1+Hfn*k*Gfn));
DEFAULT RETURN "Enter either zero (0) for open feedback or one (1) for closed (Unity) feedback system";
usrg := solveTf*(1/s);
usrg := collect(approx(usrg));
usrg := ilaplace(usrg,s,t);
dxfcn := collect(denom(solveTf));
dxfcn := cZeros(dxfcn,s);
nxfcn := collect(numer(solveTf));
nxfcn := cZeros(dxfcn,s);
roots := EVAL(mat2list(dxfcn+k*nxfcn));
ceroots := EVAL(mat2list(dxfcn));
minev := MIN(abs(RE(ceroots)));
IF (minev == 0) THEN
Tfinal := 10;
ELSE
Tfs := 7/minev;
y := 10^(CEILING(log10(Tfs))-1);
Tfinal := y*CEILING(Tfs/y);
ese := string(usrg);
ese := REPLACE(ese,"t","X");
ese := cat("(", ese, ")", "*Heaviside(X)");
F2 := ese;
Yfinal := approx(RE(F2(999999999999999999999999999999)));
IF (Yfinal > 999999999 OR Yfinal < -999999999) THEN
BREAK;
ELSE
F4 := STRING(Yfinal*0.9);
F5 := STRING(Yfinal*0.1);
F7 := STRING(Yfinal-Yfinal*0.02);
F8 := STRING(Yfinal+Yfinal*0.02);
F0 := STRING(Yfinal);
CHECK(2);
Xmin := 0;
Xmax := approx(Tfinal);
Ymin := 0;
Ymax := 999;
ELSE
Ymax := approx(1.10*Yfinal);
IF (Yfinal == 0) THEN
Ymax := 10;
RETURN "Press the Plot button to view the graph";
#end
#cas
stepInfo() :=
LOCAL Yfinal,Tfinal,Tr,Tp,Ts,perOS;
LOCAL ess,Trupper,Trlower,Tsu,Tsl,TsTwoMax,TsTwoMin;
LOCAL steplabel,stepval,stepinfo,xsteplist,ysteplist,dt;
Tfinal := Xmax;
Tr := ∞;
Tp := ∞;
Tpvalue := ∞;
Ts := ∞;
Tsvalue := ∞;
perOS := ∞;
Yfinal := ∞;
ess := ∞;
ELSE
ess := (1-Yfinal)*100;
xsteplist := {};
ysteplist := {};
dt := 0.1;
FOR q FROM 0 TO Tfinal STEP dt DO
xsteplist := CONCAT(xsteplist,q);
ysteplist := CONCAT(ysteplist,F2(q));
Tp := MAX(ysteplist);
Tpvalue := POS(ysteplist,Tp);
Tpvalue := approx(xsteplist(Tpvalue));
Tpvalue := EXTREMUM(F2(X),Tpvalue);
IF (Tp <= Yfinal) THEN
Tp := Yfinal;
ELSE
Tp := subst(F2(x),x = Tpvalue);
Trupper := MIN(solve(F2(X)=Yfinal*0.9,X=0..Tpvalue));
Trlower := MIN(solve(F2(X)=Yfinal*0.1,X=0..Tpvalue));
Tr := Trupper - Trlower;
Tsu := (Yfinal+(Yfinal*0.02));
Tsl := (Yfinal-(Yfinal*0.02));
TsTwoMax := solve(F2(X)=Tsu,X = 0 .. Tfinal);
TsTwoMin := solve(F2(X)=Tsl,X = 0 .. Tfinal);
Ts := MAX(CONCAT(TsTwoMin, TsTwoMax));
Tsvalue := F2(Ts);
IF (Tp > Yfinal) THEN
perOS := ((Tp-Yfinal)/(Yfinal))*100;
ELSE
perOS := 0;
steplabel := list2mat(["Rise Time (Tr)","Peak Time (Tp)", "Peak Value","Settling Time (Ts)", "Settling Value","Percent Overshoot","Final Value"],1);
stepval := [Tr,Tpvalue,Tp,Ts,Tsvalue,perOS,Yfinal];
REPLACE(stepval,2,[∞]);
stepinfo := ADDCOL(steplabel,stepval,2);
RETURN stepinfo;
#end